We have several of these contraptions.  Most of them we install sprinklers
in.  One in the top of the unit, because they always seem to have solid
top, and one under the ferris wheel (intermediate level head here) due to
the blockage from above.  The manufacturer does not seem to acknowledge the
fire hazard with these things and is not much help with sprinkler
installation.  They can tell you where not to cut into the panels so as to
avoid the drive mechanisms but have no standard installation devices to
assist in installing sprinklers.

As to whether sprinklers are required, NFPA 13 has the criteria for
sprinklers when obstructions exist to the overhead sprinklers.  These
things are almost always more than 4 feet wide so present an obstruction.
No, it doesn't specifically mention carousels, but there is usually a
tremendous quantity of combustibles in these things.   Without sprinkler
protection you have a huge fire exposure before it breaks out and gets the
ceiling system involved.

Maybe you can get them to take the top off the carousel so it is exposed to
the overhead sprinklers.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
[email protected]


                                                                                
                                       
  From:       <[email protected]>                                            
                                       
                                                                                
                                       
  To:         <[email protected]>                                
                                       
                                                                                
                                       
  Date:       02/26/2010 10:24 AM                                               
                                       
                                                                                
                                       
  Subject:    Carousel Storage Units                                            
                                       
                                                                                
                                       
  Sent by:    [email protected]                          
                                       
                                                                                
                                       





I've been searching NFPA 13 for info on protection of these type of storage
units.   They are typically fully enclosed, have rows of plastic bins which
are linked together by a drive mechanism, often computer indexed to an
operator can enter a part number and the rows of bins rotate until the
appropriate row is at the operator opening for access.  They can be of any
size, we're looking at about 10-15 feet wide, about 5-10 ft deep and about
20 ft tall.  The parts in the plastic bins are supposed to be mostly
non-combustible (they used the term mostly and that's all they'll share).

http://www.kardexremstar.com/content/products/vertical/

I can't find anything in 13, so either the Standard doesn't address these
or I'm using the wrong term.

I do know there is an FM Data Sheet on them but we are directed not to
follow FM data.  This is a foreign client who insists that if it's not in
the Building or Fire code they are not going to do it regardless of who
says to do what.  I can't argue with that but I do need to make sure the
situation has been addressed.


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to