We have several of these contraptions. Most of them we install sprinklers in. One in the top of the unit, because they always seem to have solid top, and one under the ferris wheel (intermediate level head here) due to the blockage from above. The manufacturer does not seem to acknowledge the fire hazard with these things and is not much help with sprinkler installation. They can tell you where not to cut into the panels so as to avoid the drive mechanisms but have no standard installation devices to assist in installing sprinklers.
As to whether sprinklers are required, NFPA 13 has the criteria for sprinklers when obstructions exist to the overhead sprinklers. These things are almost always more than 4 feet wide so present an obstruction. No, it doesn't specifically mention carousels, but there is usually a tremendous quantity of combustibles in these things. Without sprinkler protection you have a huge fire exposure before it breaks out and gets the ceiling system involved. Maybe you can get them to take the top off the carousel so it is exposed to the overhead sprinklers. John Hoffman P.E. | Fire Protection Engineer | Facility Engineering Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear Security Administration's Kansas City Plant | Operated by Honeywell FM&T | 2000 E. 95th St | Kansas City, MO 64131 | ph 816-997-7213 | [email protected] From: <[email protected]> To: <[email protected]> Date: 02/26/2010 10:24 AM Subject: Carousel Storage Units Sent by: [email protected] I've been searching NFPA 13 for info on protection of these type of storage units. They are typically fully enclosed, have rows of plastic bins which are linked together by a drive mechanism, often computer indexed to an operator can enter a part number and the rows of bins rotate until the appropriate row is at the operator opening for access. They can be of any size, we're looking at about 10-15 feet wide, about 5-10 ft deep and about 20 ft tall. The parts in the plastic bins are supposed to be mostly non-combustible (they used the term mostly and that's all they'll share). http://www.kardexremstar.com/content/products/vertical/ I can't find anything in 13, so either the Standard doesn't address these or I'm using the wrong term. I do know there is an FM Data Sheet on them but we are directed not to follow FM data. This is a foreign client who insists that if it's not in the Building or Fire code they are not going to do it regardless of who says to do what. I can't argue with that but I do need to make sure the situation has been addressed. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)