Just finished bidding a project at Ft. Carson with one of these and option
of 3. They are available without top's. The warehouse they were in was ESFR,
and that coverage extended over the open top of these carousels.
Later an addendum came out asking for charge to have covered tops and
internal sprinkler protection, with no spec. for density or location or type
of layout required. We contacted the MFG. that had these all over the world
for the military, and said that every system was sort of done different. We
ended up with an allowance for this alternate, pending "Engineering"
guidance.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926




Maybe you can get them to take the top off the carousel so it is exposed to
the overhead sprinklers.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
)