Referencing the 2010 edition, by Table/Figure 8.9.5.1.3, you have an obstruction (assuming I'm correctly understanding your situation). Byt those figures, your head would need to be no more than 1 inch above the bottom of the bulkhead (not 18 as you've described).
I must admit this is more stringent than I would have assumed off-hand. Mark A. Sornsin, PE Fire Protection Engineer Ulteig Engineers, Inc. Fargo, ND Direct: 701. 280.8591 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of A.P.Silva Sent: Friday, February 26, 2010 1:45 PM To: [email protected] Subject: RE: sidewall obstruction NFPA 13 Care Facility with patient rooms protected with residential sidewall heads. The room is 14' wide x 11'-6" long. The sidewall head on the 14' wide wall. On the far side of the s/w head is a bulkhead (parallel to the 14' wall) 2'-6" wide (horizontal) and 2 feet deep (vertical). So that makes the near edge of the bulkhead 9 feet from the head and the bottom of it 18" below the sprinkler deflector (assuming it is 6" below the ceiling). Is the bulkhead an obstruction? Long time ago I asked a similar question from Reliable and Tyco. Reliable never got back to me. Tyco took a long time to reply, and then said yes, it was an obstruction. Tony _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)