Okay, now if the bulkhead is only 6" wide (instead of 2'-6") and the near
edge of the bulkhead is still 9' away from the s/w head, is it still an
obstruction? 

My view is that the NFPA table and manufacturer's installation manuals are
primarily when the s/w head has to cover considerably past the obstruction,
such as when the obstruction is not against the wall. So I think there shoud
be a distance past the obstruction associated with these tables. To make it
ridiculous, say the bulkhead is 1 inch wide, say a decorative moulding on
the wall. Would that be an obstruction?

When I asked these questions from Tyco, they referred me to the table and
said it was an obstruction.

Tony   

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mark Sornsin
Sent: February 26, 2010 1:23 PM
To: '[email protected]'
Subject: RE: sidewall obstruction

Referencing the 2010 edition, by Table/Figure 8.9.5.1.3, you have an
obstruction (assuming I'm correctly understanding your situation). Byt those
figures, your head would need to be no more than 1 inch above the bottom of
the bulkhead (not 18 as you've described).

I must admit this is more stringent than I would have assumed off-hand.

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
Direct:    701. 280.8591


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Friday, February 26, 2010 1:45 PM
To: [email protected]
Subject: RE: sidewall obstruction


NFPA 13 Care Facility with patient rooms protected with residential sidewall
heads. The room is 14' wide x 11'-6" long. The sidewall head on the 14' wide
wall. On the far side of the s/w head is a bulkhead (parallel to the 14'
wall) 2'-6" wide (horizontal) and 2 feet deep (vertical). So that makes the
near edge of the bulkhead 9 feet from the head and the bottom of it 18"
below the sprinkler deflector (assuming it is 6" below the ceiling). Is the
bulkhead an obstruction?

Long time ago I asked a similar question from Reliable and Tyco. Reliable
never got back to me. Tyco took a long time to reply, and then said yes, it
was an obstruction.

Tony

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to