One of the difficulties we've been running into when trying to estimate the 
pump size is water departments using computer modeling to determine the 
anticipated water flow at a site.  So you give it your best guess then when the 
water lines are run and the flow begins (usually loooong after you're off the 
project) it's discovered that the actual flow conditions don't match the 
modeled conditions.  Most contractors have already ordered the pump on day one 
to get it there on time so there's no backing up.  Since the A/E firms don't in 
most cases do any detailed design you are forced to give it your best shot and 
put in the specs that the criteria be verified based on final sprinkler 
hydraulic demands.  But it almost never happens in that order.  

So when the actual supply comes in too low or too high for the pump selection, 
things get added to the system during startup.




Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Tuesday, April 06, 2010 11:05 AM
To: [email protected]
Subject: Re: Pressure relief valves to flatten the pump curve

One situation we ran into recently: A pump, fed from the public supply, had 
been installed with a churn pressure right at 175 psi. 
Subsequent upgrades added 15-20 psi to the public and now the churn was 190+. 
They adjusted the relief valve to keep the pressure down to the 175. I happened 
to witness the annual pump test plus one of the weekly 10 minute tests. I 
metered what I could and figured that they probably dump 250,000 gallons in the 
parking lot over the course of a year. Most water department don't like that 
(especially when it is not metered). They ended up replacing the pump earlier 
this year.

Wouldn't a variable speed controller be a better alternative? 
(assuming an existing pump)



At 10:29 AM 4/6/2010, you wrote:
>IT has obviously gained legitimacy through longevity in their eyes.
>IT NEVER was a good idea to really on a mechanic device instead of 
>properly sizing the pump and/or using the appropriate components.
>That's like having a car engine staying rev'd up and engaged and 
>relying on the brake to overcome it. Who would do that - intentionally 
>anyways?
>
>The argument that 20 never previously said you could not do it is a 
>weak basis.  The standards seldom say DON"T DO A BAD PRACTICE.  The 
>exception is when something starts becoming too prevalent.  The 
>standard never said over design then rely on a relief valve.  Saying 
>use a relief valve if the pressure is too high is not the same as 
>saying use a relief valve to offset poor design.  JUst because many 
>casually did it does not make it a sound design but old habits are hard 
>to kick especially bad habits.
>
>The primary reasons that comes to mind have been expressed in other 
>messages.  Good suggestion by George to review the ROP/ROC which are 
>available for the last several cycles on the NFPA website.  If it is 
>older than what is available their library can send you the info.
>
>Roland
>
>On Apr 5, 2010, at 12:36 PM, Frans Stoop wrote:
>
> > Roland,
> >
> > The technicians that I have to communicate with don't take "it's a 
> > very bad thing" for an answer.
> > They like to know why it is so bad. They even don't take the wording 
> > "shall not be used" as it is in the current NFPA 20 edition as a 
> > sufficient reason not to do it.
> >
> > Regarding the past: there was no reference in the 1996 edition of 
> > NFPA 20 about not using the pressure relief valve to limit the 
> > maximum pressure.
> > Even the Fire Pump Handbook (1998) makes no reference to this issue 
> > in its commentary text.
> >
> > The first appearance that I found is in the Appendix of the 1999 
> > edition where it is called "poor design practice".
> >
> > In today's edition the wording "shall not be used" is in the main 
> > text.
> > My reasoning is that somewhere between 1999 and today the committee 
> > must have had good reasons to decide to change the wording and 
> > forbid the use of the pressure relief valve to limit the pressure. 
> > I'm curious what that reasons could be.
> >
> > Regarding dumping the water in the parking lot: The cases I refer to 
> > are mainly industrial plants. The fire water is usually taken from a 
> > large suction tank. The discharge of the pressure relief valve is 
> > piped back to the top of that tank. So nobody is troubled by the 
> > discharge and the water is not wasted.
> >
> > The high pressure in the point of operation happens when there are 
> > one or more design areas on a high elevated places (like happens e.g.
> > in power plants). At the same time there are components on ground 
> > level that are only available in 175 psi design (like dry pendents 
> > and ESFR sprinklers).
> > There are quite a lot of watersupplies overhere that use the 
> > pressure relief valve for this purpose if a high operating pressure 
> > is required. And what worries me more: even in new installations it 
> > seems still a popular way to limit the pressure.
> >
> > However, thank you for sharing your point of view.
> >
> > Frans Stoop
> > TOS architecture & fire protection
> > Netherlands <[email protected]>
> > Tel. +31-24-324 0112
> >
> > At 09:42 2-4-2010 -0700, you wrote:
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to