NFPA 13, 2007 section A.11.2.3.1.8 (9). Doesn't it appear to require inside
hose allowance to be added to the sprinkler demand at the point of
connection?

Tony 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: April 8, 2010 2:39 PM
To: [email protected]
Subject: Re: Water Supply

WHat does the presence of the 2-1/2 have to do with this issue (unless  
you are supply the standpipe supply per 14)?   The sprinkler calc does  
not include an inside hose demand for hose connections on a standpipe.

Roland

On May 9, 2010, at 12:31 PM, A.P.Silva wrote:

> The building code here says the water supply need not satisfy the IFC 
> fire flow if the building is sprinklered. There will also be 
> standpipes in the building with 2 1/2" hose valves.
>
> Tony
>