NFPA 13, 2007 section A.11.2.3.1.8 (9). Doesn't it appear to require inside hose allowance to be added to the sprinkler demand at the point of connection?
Tony -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Roland Huggins Sent: April 8, 2010 2:39 PM To: [email protected] Subject: Re: Water Supply WHat does the presence of the 2-1/2 have to do with this issue (unless you are supply the standpipe supply per 14)? The sprinkler calc does not include an inside hose demand for hose connections on a standpipe. Roland On May 9, 2010, at 12:31 PM, A.P.Silva wrote: > The building code here says the water supply need not satisfy the IFC > fire flow if the building is sprinklered. There will also be > standpipes in the building with 2 1/2" hose valves. > > Tony > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)