WHat does the presence of the 2-1/2 have to do with this issue (unless  
you are supply the standpipe supply per 14)?   The sprinkler calc does  
not include an inside hose demand for hose connections on a standpipe.

Roland

On May 9, 2010, at 12:31 PM, A.P.Silva wrote:

> The building code here says the water supply need not satisfy the  
> IFC fire
> flow if the building is sprinklered. There will also be standpipes  
> in the
> building with 2 1/2" hose valves.
>
> Tony
>