Brad-
Unfortunately I don't have access to that Standard, would it be a big pain
in the @$$ to email me that one section? Another question I have is if the
plans were approved by the Architect, Engineer, and local AHJ with the line
passing through the room wouldn't that at least be grounds for a possible
change order?


Brian Harris
FDFP INC.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Sent: Monday, May 24, 2010 10:34 AM
To: [email protected]
Subject: RE: Elevator Equipment Rooms

Do you have access to ASME A17.1 Elevator Code? 2.8.2.3 (requires some
interpretation but) I think the intent is only piping serving the head(s) in
the room is allowed.

-----Original Message-----
From: Brian Harris [mailto:[email protected]]
Sent: Monday, May 24, 2010 9:01 AM
To: [email protected]
Subject: Elevator Equipment Rooms

 
Good Morning Gents:
Quick question regarding Elevator Equipment Rooms: is it permissible for a
sprinkler line to pass through the equipment room? The line supply's the
head in the room (which is shunt trip protected) and also a couple other
heads in the adjacent rooms. The GC is telling me that the elevator company
is telling him that the state elevator inspector will turn down the
installation because the head in the equipment room needs to be on it's own
separate line... Any help? 

Regards,

bh

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to