Brian, I mis-spoke about the shunt trip thing- what I was wondering is do you have a control valve for the head(s) in the Elev. Equip. Rm.? (usually located outside the room so the head(s) can be turned off with-out going in there) This I think would be the main reason for not going through and feeding other heads. The QR in EH thing: it is not allowed when the density/area method is used (to prevent a ton of heads from going off I guess), so it would not apply to 1 head in a pit, right? AHJ: "You DID use the density/area method, 3rd floor, east side, your "Calc Area #1". :)
-----Original Message----- From: Brian Harris [mailto:[email protected]] Sent: Tuesday, May 25, 2010 7:33 AM To: [email protected]; [email protected] Subject: RE: Elevator Equipment Rooms Brad- The only head that's on the shunt trip is the one in the equipment room, the others are standard heads in a LH area.... Brian Harris FDFP INC. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Brad Sent: Monday, May 24, 2010 5:36 PM To: [email protected]; [email protected] Subject: RE: Elevator Equipment Rooms Also, like I said, it might not be the latest, and your local people might have modified it. The 'letter' of the code allows it I think, but I go by one code I call the 2010 edition of B.O.S.S. Are the other couple of heads on the shunt too? I would use standard response high temp heads in the Elev. Equip.-- you want the heat detector going off before the head. And the head in the pit should be SR high temp-- flammable liquid is EH, and you cannot use QR in EH. -----Original Message----- From: Brad [mailto:[email protected]] Sent: Monday, May 24, 2010 4:00 PM To: [email protected] Subject: RE: Elevator Equipment Rooms Brian, Would you be able to post that section I e-mailed you- (the relevant parts)- it is a little vague, and some feed-back from the pros here might help you- I would do it but I do not know how -----Original Message----- From: Brian Harris [mailto:[email protected]] Sent: Monday, May 24, 2010 3:55 PM To: [email protected] Subject: RE: Elevator Equipment Rooms Thom- No need to be a smart @$$..... Brian Harris FDFP INC. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Thom McMahon Sent: Monday, May 24, 2010 4:42 PM To: [email protected] Subject: RE: Elevator Equipment Rooms Yes one could! And you might prevail, at least for a while just like the argument that the Earth is Flat. With limited information it sure seemed so for a while, but my what a beautiful blue round planet we live on. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Brian Harris Sent: Monday, May 24, 2010 11:05 AM To: [email protected] Subject: RE: Elevator Equipment Rooms Thom- One could argue that 8.15.5.5. is only talking about heads at the top of hoistways..... Brian Harris FDFP INC. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)