Brian ,
The safe approach to these rooms is always to enter them only to serve the 
sprinkler in that room . It keeps down problems of interpretation,etc. between 
the AHJ , elevatore inspectors , etc. As to the issue of having an approved 
drawing , most approval stamps are equipped with the statement of "subject to 
field inspection" whereas these items are normally found.

Lamar V.


---- Brian Harris <[email protected]> wrote: 
> Brad-
> Unfortunately I don't have access to that Standard, would it be a big pain
> in the @$$ to email me that one section? Another question I have is if the
> plans were approved by the Architect, Engineer, and local AHJ with the line
> passing through the room wouldn't that at least be grounds for a possible
> change order?
> 
> 
> Brian Harris
> FDFP INC.
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Brad
> Sent: Monday, May 24, 2010 10:34 AM
> To: [email protected]
> Subject: RE: Elevator Equipment Rooms
> 
> Do you have access to ASME A17.1 Elevator Code? 2.8.2.3 (requires some
> interpretation but) I think the intent is only piping serving the head(s) in
> the room is allowed.
> 
> -----Original Message-----
> From: Brian Harris [mailto:[email protected]]
> Sent: Monday, May 24, 2010 9:01 AM
> To: [email protected]
> Subject: Elevator Equipment Rooms
> 
>  
> Good Morning Gents:
> Quick question regarding Elevator Equipment Rooms: is it permissible for a
> sprinkler line to pass through the equipment room? The line supply's the
> head in the room (which is shunt trip protected) and also a couple other
> heads in the adjacent rooms. The GC is telling me that the elevator company
> is telling him that the state elevator inspector will turn down the
> installation because the head in the equipment room needs to be on it's own
> separate line... Any help? 
> 
> Regards,
> 
> bh
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to