Brad-
The only head that's on the shunt trip is the one in the equipment room, the
others are standard heads in a LH area.... 


Brian Harris
FDFP INC.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Sent: Monday, May 24, 2010 5:36 PM
To: [email protected]; [email protected]
Subject: RE: Elevator Equipment Rooms

Also, like I said, it might not be the latest, and your local people might
have modified it. The 'letter' of the code allows it I think, but I go by
one code I call the 2010 edition of B.O.S.S.
Are the other couple of heads on the shunt too? I would use standard
response high temp heads in the Elev. Equip.-- you want the heat detector
going off before the head. And the head in the pit should be SR high temp--
flammable liquid is EH, and you cannot use QR in EH.

-----Original Message-----
From: Brad [mailto:[email protected]]
Sent: Monday, May 24, 2010 4:00 PM
To: [email protected]
Subject: RE: Elevator Equipment Rooms

Brian,

Would you be able to post that section I e-mailed you- (the relevant parts)-
it is a little vague, and some feed-back from the pros here might help you-
I would do it but I do not know how

-----Original Message-----
From: Brian Harris [mailto:[email protected]]
Sent: Monday, May 24, 2010 3:55 PM
To: [email protected]
Subject: RE: Elevator Equipment Rooms

Thom-
No need to be a smart @$$..... 


Brian Harris
FDFP INC.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Monday, May 24, 2010 4:42 PM
To: [email protected]
Subject: RE: Elevator Equipment Rooms

Yes one could! And you might prevail, at least for a while just like the
argument that the Earth is Flat. With limited information it sure seemed so
for a while, but my what a beautiful blue round planet we live on.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Monday, May 24, 2010 11:05 AM
To: [email protected]
Subject: RE: Elevator Equipment Rooms

Thom-
One could argue that  8.15.5.5. is only talking about heads at the top of
hoistways.....


Brian Harris
FDFP INC.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to