Not only will the drum have initial system pressure on it when removing the
plug - even after the top valve is closed, but you may have an instance
where you have to alternate opening and closing the valves more than one
time if there is more condensate/water than will fit in drum at that time.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
[email protected]
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mike
Hairfield
Sent: Tuesday, July 13, 2010 10:50 AM
To: AFSA SprinklerFORUM
Subject: RE: Drum Drip- why 2 valves?


Too many Rookies on here!!!!!

 

It's also called a condensate nipple and you use both valves when draining
off the

water by removing the plug, leave the bottom valve shut, open the top valve

let the water drain into it, shut the top valve and then drain off the
water.

 

Keep doing this until there is no longer any water in the condensate nipple
(drum drip)

 

Mike
 
> Subject: RE: Drum Drip- why 2 valves?
> Date: Tue, 13 Jul 2010 10:43:51 -0500
> From: [email protected]
> To: [email protected]; [email protected]
> 
> Brad,
> 
> If the container is plugged and the top valve open, it is exposed to
> system pressure which could be anything from 10 to 50 psi. That plug
> would be under that pressure and pose a dangerous removal.
> 
> Regards,
> 
> Tim Frankenberg
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Brad
> Sent: Tuesday, July 13, 2010 10:38 AM
> To: [email protected]; 'Sprinklerforum'
> Subject: RE: Drum Drip- why 2 valves?
> 
> But with the top valve closed, there is no system pressure.
> 
> -----Original Message-----
> From: [email protected] [mailto:[email protected]] 
> Sent: Tuesday, July 13, 2010 10:35 AM
> To: Sprinklerforum; [email protected]
> Subject: Re: Drum Drip- why 2 valves?
> 
> Limit the volume trapped when you pull the plug. WIth out it, it makes
> mess
> and can be dangerous if the system has high pressure for some reason.
> Sent from my BlackBerryR smartphone with Nextel Direct Connect
> 
> -----Original Message-----
> From: "Brad" <[email protected]>
> Sender: [email protected]
> Date: Tue, 13 Jul 2010 10:27:40 
> To: <[email protected]>
> Reply-To: [email protected], [email protected]
> Subject: Drum Drip- why 2 valves?
> 
> Why is the 'bottom' valve req'd? The 'top' valve is normally open--
> close
> it, remove the plug, drain the drum, replace the plug, open the valve.
> 
> Is there some practical reason for the bottom valve? 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - www.avg.com 
Version: 9.0.830 / Virus Database: 271.1.1/3002 - Release Date: 07/13/10
01:36:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to