the reason is quite simply so the system doesn't trip, opening the upper
valve causes SLIGHT loss of psi, and lets trapped water fill the barrel,
hence the 2" size, close the top valve open the bottom valve and drain the
water, repeat as needed to drain that portion.  If you only had one valve
then the valve would trip, hence it's a maintenance drain.

On Tue, Jul 13, 2010 at 12:35 PM, Richard Mote <[email protected]>wrote:

> 30 gallon drum welded to a hand truck with a hose bib welded toward the
> bottom so we could run a hose to the nearest floor drain. These building
> were mostly open to the elements so they had a lot of floor drains.
>
> Richard L. Mote ET
> Designeer
> Rowe Sprinkler Systems, Inc.
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Byron Blake
> Sent: Tuesday, July 13, 2010 12:13 PM
> To: [email protected]
> Subject: Re: Drum Drip- why 2 valves?
>
> Open, close, open, close, open, close dump 5 gallon bucket open close open
> close open close dump 5 gallon bucket open close open close open close dump
> 5 gallon bucket.
>
> Byron
>
>
> --------------------------------------------------
> From: "Bobby Gillett" <[email protected]>
> Sent: Tuesday, July 13, 2010 11:59
> To: <[email protected]>
> Subject: RE: Drum Drip- why 2 valves?
>
> > Not only will the drum have initial system pressure on it when removing
> > the
> > plug - even after the top valve is closed, but you may have an instance
> > where you have to alternate opening and closing the valves more than one
> > time if there is more condensate/water than will fit in drum at that
> time.
> >
> > Bobby Gillett
> > Sr. Project Manager
> > Key Fire Protection, Inc.
> > (731) 424-0130 office  (731) 424-9285 fax
> > (731) 267-4853 cell
> > [email protected]
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of Mike
> > Hairfield
> > Sent: Tuesday, July 13, 2010 10:50 AM
> > To: AFSA SprinklerFORUM
> > Subject: RE: Drum Drip- why 2 valves?
> >
> >
> > Too many Rookies on here!!!!!
> >
> >
> >
> > It's also called a condensate nipple and you use both valves when
> draining
> > off the
> >
> > water by removing the plug, leave the bottom valve shut, open the top
> > valve
> >
> > let the water drain into it, shut the top valve and then drain off the
> > water.
> >
> >
> >
> > Keep doing this until there is no longer any water in the condensate
> > nipple
> > (drum drip)
> >
> >
> >
> > Mike
> >
> >> Subject: RE: Drum Drip- why 2 valves?
> >> Date: Tue, 13 Jul 2010 10:43:51 -0500
> >> From: [email protected]
> >> To: [email protected]; [email protected]
> >>
> >> Brad,
> >>
> >> If the container is plugged and the top valve open, it is exposed to
> >> system pressure which could be anything from 10 to 50 psi. That plug
> >> would be under that pressure and pose a dangerous removal.
> >>
> >> Regards,
> >>
> >> Tim Frankenberg
> >>
> >> -----Original Message-----
> >> From: [email protected]
> >> [mailto:[email protected]] On Behalf Of Brad
> >> Sent: Tuesday, July 13, 2010 10:38 AM
> >> To: [email protected]; 'Sprinklerforum'
> >> Subject: RE: Drum Drip- why 2 valves?
> >>
> >> But with the top valve closed, there is no system pressure.
> >>
> >> -----Original Message-----
> >> From: [email protected] [mailto:[email protected]]
> >> Sent: Tuesday, July 13, 2010 10:35 AM
> >> To: Sprinklerforum; [email protected]
> >> Subject: Re: Drum Drip- why 2 valves?
> >>
> >> Limit the volume trapped when you pull the plug. WIth out it, it makes
> >> mess
> >> and can be dangerous if the system has high pressure for some reason.
> >> Sent from my BlackBerryR smartphone with Nextel Direct Connect
> >>
> >> -----Original Message-----
> >> From: "Brad" <[email protected]>
> >> Sender: [email protected]
> >> Date: Tue, 13 Jul 2010 10:27:40
> >> To: <[email protected]>
> >> Reply-To: [email protected], [email protected]
> >> Subject: Drum Drip- why 2 valves?
> >>
> >> Why is the 'bottom' valve req'd? The 'top' valve is normally open--
> >> close
> >> it, remove the plug, drain the drum, replace the plug, open the valve.
> >>
> >> Is there some practical reason for the bottom valve?
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email
> >> to:[email protected]<to%[email protected]>
> >> (Put the word unsubscribe in the subject field)
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email
> >> to:[email protected]<to%[email protected]>
> >> (Put the word unsubscribe in the subject field)
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> >> (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> > (Put the word unsubscribe in the subject field)
> >
> > No virus found in this incoming message.
> > Checked by AVG - www.avg.com
> > Version: 9.0.830 / Virus Database: 271.1.1/3002 - Release Date: 07/13/10
> > 01:36:00
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> > (Put the word unsubscribe in the subject field)
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>



-- 
Tom Poisal, CET
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to