Coefficient of Thermal Expansion
 
Carbon Steel:   6.7 x 10^-6  (or 0.0000067)
Copper:  9.3 x 10^-6
PVC:  28 x 10^-6
Wood, fir:  2.1 x 10^-6
Wood, oak parallel to grain:  3.0 x 10^-6

In all cases multiply the coefficient times the length of the pipe in feet and 
the temp change in degrees F.  The result will be in feet of expansion, so 
multiply by 12 to get inches.
 
In your case, the steel pipe is expanding 2 to 3 times more than your wooden 
walkway.  Since it is a floating dock, you will need to have flexible 
connections, or swing joints at the top and bottom of your walkway anyhow.  
That might be enough to accomodate the expansion.  How much rise/fall will your 
dock have relative to the shore platform?  I recall awhile back that someone 
recommended a flex connector (Thom, maybe?) that had been used successfully in 
such a situation.
 
Note the much, much higher coefficient for PVC.  (I could not find CPVC 
quickly, but expect it to be comparable.)  This would explain George's snaky 
CPVC piping installation for which he did not get all his due.
 

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 




--- On Wed, 11/10/10, Coastal <[email protected]> wrote:


From: Coastal <[email protected]>
Subject: Re: Pipe Expansion
To: "Fletcher, Ron" <[email protected]>
Date: Wednesday, November 10, 2010, 6:41 PM


Hello Ron,

It is not a building, Wooden walkway to a floating dock.

Wednesday, November 10, 2010, 5:16:36 PM, you wrote:

> Since the building and the sprinkler system are subject to the same
> ambient conditions wouldn't the expansion rates kind of offset each
> other?

> Ron Fletcher
> Aero Automatic
> Phoenix, AZ  

> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Thom
> Sent: Wednesday, November 10, 2010 3:04 PM
> To: [email protected]; [email protected]
> Subject: RE: Pipe Expansion

> Also remember that a simple change in direction can provide the same
> protection as a full expansion loop.


> Subject: Re: Pipe Expansion

> The expansion is the expansion no matter what fittings are employed,
> well on
> unrestrained steel.  A fitting does not in itself restrain the pipe.
> Either
> the pipe moves or the want to move is translated into some internal
> force.
> The effect of the expansion it dependent on the fittings and the
> restraintment.  

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

> For Technical Assistance, send an email to: [email protected]

> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

> For Technical Assistance, send an email to: [email protected]

> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)



-- 
Best regards,
Charles Thurston
Coastal Fire Protection
Coastal                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to