How about let the grooved couplings take care of the expansion. We have done some calculations on similar situations and found the amount of expansion is negligible when you consider its environment. After all it's an ambient system that will change temperature along with everything else. We have installed runs or 6" and 8" over 1500 ft long in ambient warehouses with no allowance for expansion other than the couplings. They are still there and we have yet to receive a phone call saying they are coming apart.
By the way an 1/8" per coupling over 900 ft. is about 5.5". Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Charles Thurston Sent: Wednesday, December 01, 2010 2:55 PM To: sprinklerforum Subject: Pipe Expansion Hello sprinklerforum, I have it figured my about straight run of 900 feet of 6" Schedule 40 pipe on a Horizontal Manual Dry Standpipe is going to get about 5.5 inches longer due to thermal expansion. What have my fellow forumites used for thermal expansion joints in the past? Metraflex Seismic loops are rather expensive for this. The Project engineer is trying to request to allow for 4" every 200 feet. I want to refute his request. -- Best regards, Charles Thurston mailto:[email protected] Coastal Fire Protection/ Myrtle Beach Fire & Safety Group. AFAA Guest Electronic Privacy Notice: This e-mail, and any attachments, contains information that is, or may be, covered by electronic communications privacy laws, and is also confidential and proprietary in nature. If you are not the intended recipient, please be advised that you are legally prohibited from retaining, using, copying, distributing, or otherwise disclosing this information in any manner. Instead, please reply to the sender that you have received this communication in error, and then immediately delete it. Thank you in advance for your cooperation _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)