Nobody liked the pressure reducing valve? What if you put it in front of the 
dry pipe valve?

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, November 11, 2010 3:44 PM
To: [email protected]
Subject: RE: High Pressure Dry Pendents

Is all the piping, fittings, etc.,  rated for 300 psi?  If you're worried about 
the heads, don't forget the whole system is technically rated for 175.  


Craig Prahl
CH2MHILL/SPB
864-599-4102
________________________________________
From: [email protected] 
[[email protected]] On Behalf Of David de Vries 
[[email protected]]
Sent: Wednesday, November 10, 2010 11:42 PM
To: AFSA SprinklerForum
Subject: High Pressure Dry Pendents

I have an open parking garage under a high rise.  Fire pump sized for standpipe 
demand, so it has over 200 psi at the garage level.  Most of the dry pipe 
system in the garage has uprights, but there are some finished ceiling areas 
that need dry pendents.  I have not found any dry pendents listed for more than 
175.  Suggestions?

Of course, for most of the time the system will only see the ~50 psi air, but 
when the valve trips, it will be about 215.  Am I wrong to think the DP's 
should be listed for the static system pressure?

Dave

David A. de Vries, P.E., CSP
Firetech Engineering Incorporated



--- On Wed, 11/10/10, Coastal <[email protected]> wrote:


From: Coastal <[email protected]>
Subject: Re: Pipe Expansion
To: "Fletcher, Ron" <[email protected]>
Date: Wednesday, November 10, 2010, 6:41 PM


Hello Ron,

It is not a building, Wooden walkway to a floating dock.

Wednesday, November 10, 2010, 5:16:36 PM, you wrote:

> Since the building and the sprinkler system are subject to the same
> ambient conditions wouldn't the expansion rates kind of offset each
> other?

> Ron Fletcher
> Aero Automatic
> Phoenix, AZ

> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Thom
> Sent: Wednesday, November 10, 2010 3:04 PM
> To: [email protected]; [email protected]
> Subject: RE: Pipe Expansion

> Also remember that a simple change in direction can provide the same
> protection as a full expansion loop.


> Subject: Re: Pipe Expansion

> The expansion is the expansion no matter what fittings are employed,
> well on
> unrestrained steel.  A fitting does not in itself restrain the pipe.
> Either
> the pipe moves or the want to move is translated into some internal
> force.
> The effect of the expansion it dependent on the fittings and the
> restraintment.

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

> For Technical Assistance, send an email to: [email protected]

> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

> For Technical Assistance, send an email to: [email protected]

> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)



--
Best regards,
Charles Thurston
Coastal Fire Protection
Coastal                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to