Interesting! A 2' perimeter open to above is kind of like the opposite of a
floor opening, where we put water curtains. With no sprinklers above, the
fire should not SPREAD from the wall toward the middle more than a few feet.
A draft stop all the way around with heads on the inside at 6' seems a
little much, but has precedent. If you sprinkler around the opening up
above, what is your deflector distance? If it is 12", as the ceiling steps
down, the head above gets farther from the heat. You know the heat is going
to be a few inches above the opening- so using the same logic as with rack
sprinklers, wouldn't that be the best deflector (bulb) location? Now there
are two weird things to get approved...   

-----Original Message-----
From: Jimmy Waite [mailto:[email protected]] 
Sent: Tuesday, December 14, 2010 7:52 AM
To: [email protected]
Subject: Ceiling "Clouds

I know this has been talked about before, but I am having trouble getting
onto the archives.  

I have a situation in an auditorium/lecture hall that has a ceiling that
steps down as you get closer to the front of the room.  However, there is
about a 2'-0 perimeter around the room that is open to the non-combustible
space above the ceiling.  In this case I'd be willing to sprinkle around the
opening (sort of like 8.15.1.5 in the '07), but it seems pointless to
provide coverage over this entire lowered ceiling.  Is there any code that
backs this up? I thought I've heard some, but I don't know where it is.


Thanks,

 Jimmy Waite
 Design Engineer

 [email protected]
 mobile: 919.622.7030

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to