If you can have a well with sufficient refresh and capacity, you can oversize 
the well pump and have a reliable water supply which fulfills either (1) or (4) 
depending on semantics/definitions. And what's APPROVED. We happened across a 
36" diam well with 3,000 gal in it, oversized the well pump, connected it to 
the sprinklers and a new gang bath in this housing project, and saved the 
customer $25,000.

My understanding is the same as Cliffs, but upon re-reading the original text, 
no-it does NOT say that a FIRE pump must be used, just that IF you install a 
fire pump, do it per #20.
Betcha that wasn't the intent of the committee.


George Church'
Rowe Sprinkler
[email protected]
570-837-7647

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of David Blackwell
Sent: Thursday, January 13, 2011 4:58 PM
To: [email protected]
Subject: 2010 NFPA 13R 9.3

The code text in 2010 NFPA 13R 9.3 mentions only "pump", not "fire pump" as the 
minimum standard requirement.  Is that correct?  
[I read the commentary to both 9.3 and 9.4 and began to doubt whether a 
non-fire pump could be used.  It is clear that 9.4 code requires, where used, a 
fire pump must meet NFPA 20; however, I don't read 9.3 as actually requiring a 
fire pump be used to meet the "pump" indicated in 9.3(1) or 9.3(4).]

Perhaps my brain will work better in the morning while still fresh...


Respectfully,

David W. S. Blackwell, II, PE, CFPE
Engineering 
---------------------------------------------------------------- 
Office of State Fire Marshal 
141 Monticello Trail 
Columbia, SC 29203 
Phone:  803.896.9833 
Fax:  803.896.9806 
Email:  [email protected] 
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp 
---------------------------------------------------------------- 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to