Great idea, but I don't think its going to work. The intent is for the fire 
pump and related supply to be, insofar as possible, dedicated to FP use.
Fire pumps shouldn't be run daily for domestic boosting. You're turning on a 
300 GPM pump (in a hotel) for domestic demand? Water hammer.
Variable spped would be good- in a fire pump-$$$^^

Host of issues....in 13 ARGH. 

George Church'
Rowe Sprinkler
[email protected]
570-837-7647
-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Andy
Sent: Friday, January 14, 2011 11:33 AM
To: [email protected]
Subject: RE: 2010 NFPA 13R 9.3

Does that mean we can install Fire pump sized to handle the fire and the 
domestic load? They maintain the domestic pumps better than the fire pumps.
Any body sell a fire pump approved for domestic?
Andy

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Friday, January 14, 2011 9:30 AM
To: [email protected]
Subject: RE: 2010 NFPA 13R 9.3

1994 - The NFPA 20 pump was linked to a stored water source.  A water works 
system was related to a booster pump.
1999 - NFPA 20 pump required in all cases.
2002 - Seems to track with 1999 except new paragraph 6.5.4 is added (with no 
indication it's new and no substantiation since it was part of a general manual 
of style reformatting).  The intent of the new paragraph appears to mean that 
all pumps are to be fire pumps since there is no indication this paragraph was 
anything but a formatting change.
2007 - Same as 2002.
2010 - Same as 2002.

I think the intent is NFPA 20 in all cases (except the well source) described 
by NFPA 13R since the 1999 edition.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Thursday, January 13, 2011 5:45 PM
To: [email protected]
Subject: RE: 2010 NFPA 13R 9.3

If you can have a well with sufficient refresh and capacity, you can oversize 
the well pump and have a reliable water supply which fulfills either (1) or (4) 
depending on semantics/definitions. And what's APPROVED.
We happened across a 36" diam well with 3,000 gal in it, oversized the well 
pump, connected it to the sprinklers and a new gang bath in this housing 
project, and saved the customer $25,000.

My understanding is the same as Cliffs, but upon re-reading the original text, 
no-it does NOT say that a FIRE pump must be used, just that IF you install a 
fire pump, do it per #20.
Betcha that wasn't the intent of the committee.


George Church'
Rowe Sprinkler
[email protected]
570-837-7647

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of David Blackwell
Sent: Thursday, January 13, 2011 4:58 PM
To: [email protected]
Subject: 2010 NFPA 13R 9.3

The code text in 2010 NFPA 13R 9.3 mentions only "pump", not "fire pump" as the 
minimum standard requirement.  Is that correct?  
[I read the commentary to both 9.3 and 9.4 and began to doubt whether a 
non-fire pump could be used.  It is clear that 9.4 code requires, where used, a 
fire pump must meet NFPA 20; however, I don't read 9.3 as actually requiring a 
fire pump be used to meet the "pump" indicated in 9.3(1) or 9.3(4).]

Perhaps my brain will work better in the morning while still fresh...


Respectfully,

David W. S. Blackwell, II, PE, CFPE
Engineering
----------------------------------------------------------------
Office of State Fire Marshal
141 Monticello Trail
Columbia, SC 29203
Phone:  803.896.9833
Fax:  803.896.9806
Email:  [email protected]
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp
---------------------------------------------------------------- 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to