Sure is an interesting thought though.

On Thu, Jan 13, 2011 at 2:45 PM, George Church <[email protected]> wrote:
> If you can have a well with sufficient refresh and capacity, you can oversize 
> the well pump and have a reliable water supply which fulfills either (1) or 
> (4) depending on semantics/definitions. And what's APPROVED. We happened 
> across a 36" diam well with 3,000 gal in it, oversized the well pump, 
> connected it to the sprinklers and a new gang bath in this housing project, 
> and saved the customer $25,000.
>
> My understanding is the same as Cliffs, but upon re-reading the original 
> text, no-it does NOT say that a FIRE pump must be used, just that IF you 
> install a fire pump, do it per #20.
> Betcha that wasn't the intent of the committee.
>
>
> George Church'
> Rowe Sprinkler
> [email protected]
> 570-837-7647
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of David Blackwell
> Sent: Thursday, January 13, 2011 4:58 PM
> To: [email protected]
> Subject: 2010 NFPA 13R 9.3
>
> The code text in 2010 NFPA 13R 9.3 mentions only "pump", not "fire pump" as 
> the minimum standard requirement.  Is that correct?
> [I read the commentary to both 9.3 and 9.4 and began to doubt whether a 
> non-fire pump could be used.  It is clear that 9.4 code requires, where used, 
> a fire pump must meet NFPA 20; however, I don't read 9.3 as actually 
> requiring a fire pump be used to meet the "pump" indicated in 9.3(1) or 
> 9.3(4).]
>
> Perhaps my brain will work better in the morning while still fresh...
>
>
> Respectfully,
>
> David W. S. Blackwell, II, PE, CFPE
> Engineering
> ----------------------------------------------------------------
> Office of State Fire Marshal
> 141 Monticello Trail
> Columbia, SC 29203
> Phone:  803.896.9833
> Fax:  803.896.9806
> Email:  [email protected]
> OSFM Website: http://www.llr.state.sc.us/firemarshal.asp
> ----------------------------------------------------------------
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to