In the IBC (2006 Edition) paragraph 903.4 "Sprinkler system monitoring and 
alarms", states;
All valves controlling the water supply for automatic sprinkler systems, pumps, 
tanks, water levels and temperatures, critical air pressures and water-flow 
switches on all sprinkler systems shall be electrically supervised. And 
paragraph 903.4.1 Signals, requires that;
Alarm, supervisory and trouble signals shall be distinctly different and 
automatically transmitted to an approved central station, remote supervising 
station or proprietary supervising station as defined in NFPA 72 or, when 
approved by the fire code official, shall sound an audible signal at a 
constantly attended location.

Paragraph  903.4.3 "Floor control valves" states that;
Approved supervised indicating control valves shall be provided at the point of 
connection to the riser on each floor in high-rise buildings.

The IBC does require the supervision of fire sprinkler systems especially where 
IBC sprinkler trade off are used in the design of the building.

Have a fire safe day. 



Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Thursday, January 13, 2011 3:16 PM
To: [email protected]
Subject: Re: Hydraulic Calcs

The question is not can you configure it like a system riser and call  
it at YOUR choice a system.  The question is MUST it be a system?  As  
for the components one elects to put on each floor, NFPA 13 does not  
require all the stuff shown in A.8.17.4.2(b) for a floor control valve  
(actually the criteria in 13 that the annex material is attached to is  
not about floor control valves).  Other sections indicate the type of  
supervision for floor control valves but nothing in 13 says you have  
to have it.  Now the IBC requires a control valve but then it is real  
sloppy on the alarm requirements (many things interpreted to mean a  
flow switch per floor but nada explicitly stating on it).  A tad  
amusing.

There are significant impacts on whether each floor is a system  
especially for NFPA 25.

Roland


On Jan 13, 2011, at 10:39 AM, Todd Williams wrote:

> If the floor has its own dedicated feed from the system riser, then  
> yes it can be a system. If it has a common feed with other floors,  
> then it isn't. See NFPA 13 section 3.3.21 (assuming we accept that  
> the word "system" here means sprinkler system).
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to