We do #13 systems (prisons) supplied only from domestic pump skid and a tank connected to a combined underground that supplies hydrants as well as sprinkler systems and domestic fixtures in multiple buildings. No fire pump. Isn't at 13R system connected to a domestic line with a booster pump capable of supplying the sprinkler demand the same thing?
Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Chris Cahill Sent: Friday, January 14, 2011 9:43 AM To: [email protected] Subject: Re: 2010 NFPA 13R 9.3 This is covered in NFPA 20 5.7.1 and the annex. If it has domestic use it is NOT a fire pump needing to meet ALL the requirements of 20. But what is lacking is what if any requirements should be met. There is a perfectly legal argument if you suck off some domestic water don't even open 20. Personally l'd argue this is some type of alternate method requiring an engineer to evaluate. Chris -----Original Message----- From: "Andy" <[email protected]> Sender: [email protected] Date: Fri, 14 Jan 2011 11:33:12 To: <[email protected]> Reply-To: [email protected] Subject: RE: 2010 NFPA 13R 9.3 Does that mean we can install Fire pump sized to handle the fire and the domestic load? They maintain the domestic pumps better than the fire pumps. Any body sell a fire pump approved for domestic? Andy -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bill Brooks Sent: Friday, January 14, 2011 9:30 AM To: [email protected] Subject: RE: 2010 NFPA 13R 9.3 1994 - The NFPA 20 pump was linked to a stored water source. A water works system was related to a booster pump. 1999 - NFPA 20 pump required in all cases. 2002 - Seems to track with 1999 except new paragraph 6.5.4 is added (with no indication it's new and no substantiation since it was part of a general manual of style reformatting). The intent of the new paragraph appears to mean that all pumps are to be fire pumps since there is no indication this paragraph was anything but a formatting change. 2007 - Same as 2002. 2010 - Same as 2002. I think the intent is NFPA 20 in all cases (except the well source) described by NFPA 13R since the 1999 edition. Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146-1904 410-544-3620 410-544-3032 FAX 412-400-6528 Cell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of George Church Sent: Thursday, January 13, 2011 5:45 PM To: [email protected] Subject: RE: 2010 NFPA 13R 9.3 If you can have a well with sufficient refresh and capacity, you can oversize the well pump and have a reliable water supply which fulfills either (1) or (4) depending on semantics/definitions. And what's APPROVED. We happened across a 36" diam well with 3,000 gal in it, oversized the well pump, connected it to the sprinklers and a new gang bath in this housing project, and saved the customer $25,000. My understanding is the same as Cliffs, but upon re-reading the original text, no-it does NOT say that a FIRE pump must be used, just that IF you install a fire pump, do it per #20. Betcha that wasn't the intent of the committee. George Church' Rowe Sprinkler [email protected] 570-837-7647 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of David Blackwell Sent: Thursday, January 13, 2011 4:58 PM To: [email protected] Subject: 2010 NFPA 13R 9.3 The code text in 2010 NFPA 13R 9.3 mentions only "pump", not "fire pump" as the minimum standard requirement. Is that correct? [I read the commentary to both 9.3 and 9.4 and began to doubt whether a non-fire pump could be used. It is clear that 9.4 code requires, where used, a fire pump must meet NFPA 20; however, I don't read 9.3 as actually requiring a fire pump be used to meet the "pump" indicated in 9.3(1) or 9.3(4).] Perhaps my brain will work better in the morning while still fresh... Respectfully, David W. S. Blackwell, II, PE, CFPE Engineering ---------------------------------------------------------------- Office of State Fire Marshal 141 Monticello Trail Columbia, SC 29203 Phone: 803.896.9833 Fax: 803.896.9806 Email: [email protected] OSFM Website: http://www.llr.state.sc.us/firemarshal.asp ---------------------------------------------------------------- _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)