I concur with everything you said and the alarm requirements are very explicit regarding on supervision IF a component is present. Where does the IBC say you have to have a water flow switch on EVERY floor of a hi-rise?

Roland

On Jan 13, 2011, at 12:28 PM, Jim Davidson wrote:

In the IBC (2006 Edition) paragraph 903.4 "Sprinkler system monitoring and alarms", states; All valves controlling the water supply for automatic sprinkler systems, pumps, tanks, water levels and temperatures, critical air pressures and water-flow switches on all sprinkler systems shall be electrically supervised. And paragraph 903.4.1 Signals, requires that; Alarm, supervisory and trouble signals shall be distinctly different and automatically transmitted to an approved central station, remote supervising station or proprietary supervising station as defined in NFPA 72 or, when approved by the fire code official, shall sound an audible signal at a constantly attended location.

Paragraph  903.4.3 "Floor control valves" states that;
Approved supervised indicating control valves shall be provided at the point of connection to the riser on each floor in high-rise buildings.

The IBC does require the supervision of fire sprinkler systems especially where IBC sprinkler trade off are used in the design of the building.

Have a fire safe day.



Jim Davidson

Davidson Associates
Fire Protection * Medical Gas * Code Consulting
302-994-9500   Fax:302-234-1781


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to