If the systems were drained the switches would trip when the system was 
refilled. 

The arrangement is a control valve (V), check va.(V), flow switch (F) then tee 
to a test line with a valve (X) on the test line, straight through the tee goes 
to the sprinkler.
               __X_______
____X__V__F___|_________

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Hinson, Ryan
Sent: Thursday, April 07, 2011 11:44 AM
To: '[email protected]'
Subject: RE: elevator related sprinklers

Could be to prevent the elevator machine room or elevator shaft flow switches 
from tripping if the system feeding these heads are drained.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-6003 Ext 3662

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, April 07, 2011 9:20 AM
To: [email protected]
Subject: elevator related sprinklers

UFC 3-600 shows a check valve in the line serving a sprinkler in an elevator 
machine room or hoistway.  Just wondering if anyone can state what the purpose 
of the check is in that line.  Looking at Figures 6-8 through 6-9. 

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to