I just did three this way.  I figured the check was to trap the pressure in.  
Like George said, they want no retard.

John

John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Thursday, April 07, 2011 11:56 AM
To: [email protected]
Subject: RE: elevator related sprinklers

And I believe that WFS has no retard, so trapping the high pressure surges into 
this piping minimizes potential for false trips.

George Church
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, April 07, 2011 11:51 AM
To: [email protected]
Subject: RE: elevator related sprinklers

If the systems were drained the switches would trip when the system was 
refilled. 

The arrangement is a control valve (V), check va.(V), flow switch (F) then tee 
to a test line with a valve (X) on the test line, straight through the tee goes 
to the sprinkler.
               __X_______
____X__V__F___|_________

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Hinson, Ryan
Sent: Thursday, April 07, 2011 11:44 AM
To: '[email protected]'
Subject: RE: elevator related sprinklers

Could be to prevent the elevator machine room or elevator shaft flow switches 
from tripping if the system feeding these heads are drained.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-6003 Ext 3662

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, April 07, 2011 9:20 AM
To: [email protected]
Subject: elevator related sprinklers

UFC 3-600 shows a check valve in the line serving a sprinkler in an elevator 
machine room or hoistway.  Just wondering if anyone can state what the purpose 
of the check is in that line.  Looking at Figures 6-8 through 6-9. 

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to