Craig,

I agree with what the others are saying about the check valve being
installed to reduce the chance of a false signal.  A California elevator
expert told me a few years ago that using the water flow switch to activate
the elevator power shunt trip is not recommended due to possible false
trips regardless of whether or not a check valve is installed.  Instead
they prefer to use lower temperature heat detectors to actuate the shunt
trip.

Jim


From:   <[email protected]>
To:     <[email protected]>
Date:   04/07/2011 10:56 AM
Subject:        elevator related sprinklers
Sent by:        [email protected]



UFC 3-600 shows a check valve in the line serving a sprinkler in an
elevator machine room or hoistway.  Just wondering if anyone can state what
the purpose of the check is in that line.  Looking at Figures 6-8 through
6-9.

Craig L. Prahl, CET
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to