I think section 8.5.2.1.1-2 (NFPA 13 07ed) supports your thinking when determining the area of the sprinkler.
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Cliff Whitfield Sent: Wednesday, December 07, 2011 8:35 AM To: [email protected] Subject: RE: Sprinkler spacing 101 I would say just the opposite but obviously, one of us is wrong. I was taught by Dan Mallow (boy, that makes me old!) that if the beam was such a depth that the sprinkler cannot spray under it then you treat it as a wall and space accordingly. Cliff Whitfield, SET President Fire Design, Inc. Ph: 337-261-8807 Fx: 337-261-8808 [email protected] www.fire-design.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Wednesday, December 07, 2011 8:30 AM To: [email protected] Subject: Re: Sprinkler spacing 101 I will jump in and say no, the beams cannot be treated as walls for spacing. The occupancy can be placed under the beams and go from one bay to the next, so the sprinkler spacing has to correspond. At 09:14 AM 12/7/2011, you wrote: >Warning - stupid question in 3...2...1... > >I just found myself in a strange argument about sprinkler spacing in a >box butler building Ord Group II storage to 12'0. The bay spacing >between the butler framing uprights is inconsistent, but for >conversation sake I'll simplify the concept. > >Take a bay to be 40'0, space 4 lines across for 10'0 between lines. >Take the next bay at 30'0 and throw 2 lines there with 15'0 between >lines. (Reminder: I started this with "Warning, stupid question...") >For the 40'0 bay for 10'0 between lines the heads on the line are 12'0 >for spacing of 120. For the 30'0 bay the heads on the line are 8'0 for >spacing of 120. > >Ok, with that really goofy situation set, here's the strange argument I >was in: When reviewing this design I rejected it based on the fact that >the heads spanning the beam between the bays are overspaced. (5' + >7'6) x 12' = 150sf / head. Their argument was they were spacing to the >bays only. I returned with 13-8.5.2.1 stating nothing about beams and >"bayspace" limiting the coverage at the deck. Even had to say: Imagine >your standing on the floor under the beam at the roof deck, the floor >space that we're protecting doesn't care about the beam and looking up >at the four heads your S x L doesn't care about the beam either. > >Maybe I'm just looking for clarification that I'm not completely insane. >I'm only halfway done my first coffee and I'm looking outside at snow >and had to scrape ice off my car this morning, so perhaps I'm having >issues today. But this is one argument that I never thought I'd find >myself in the middle of. To sum up a stupid question: For all >intensive purposes, can a butler framing beam (or any other deep beam >for that >matter) at the roof essentially be a "wall" for determining your area >per sprinkler? > >Mike Gallello >Confused? >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum