It DOES contradict itself. That to was fixed for the next edition (released in 2012 but called 2013 ed)

Roland

On May 9, 2012, at 11:01 AM, Dewayne Martinez wrote:

I always took 23.1.3.2 (1) to mean no combined service allowed for mains
less than 6in but I see in the appendix that it states for mains less
than 6" domestic demand should be accounted for.
Seems to contradict itself.