The retroactivity clause in NFPA 13 should allow you to leave the 3/4" pipe.q

Sent from my HTC smartphone on the Now Network from Sprint!

----- Reply message -----
From: "Jarron Gass" <[email protected]>
To: "[email protected]" <[email protected]>
Subject: 3/4" Pipe and Sprigs
Date: Fri, Jun 22, 2012 4:54 pm






Folks,

 

I am working on an older building, pipe scheduled system with ¾” pipe at the 
end of some lines as well as ¾” sprigs in some areas.  As best we can tell, the 
bulk of the system is from about 1930.  In NFPA13, 2011 edition it says the 
following:

 

22.4.1.2 Pipe sizes shall be no less than 1 in. (25 mm) nominal

for ferrous piping and 3⁄4 in. (20 mm) nominal for copper

tubing or nonmetallic piping listed for fire sprinkler service.

 

This is referencing hydraulic calculations, but I seem to recall that there was 
a requirement somewhere in the standard to remove any ¾” piping and replace 
with 1”.  If so, can anyone point me to the proper section and also, would that 
include the sprigs?  It seems a little frivolous to remove the existing 1’-0” 
long sprigs and install an extra heavy close nipple with a ¾” x 1” reducing 
coupling, a short piece of 1” pipe and another reducing coupling.

 

I appreciate any input.

 

Thanks,

 

Jarron

 

  

 

Jarron J. Gass - J. & J. Fire Protection Co., Inc.

101 Powell Rd., Butler, PA 16002, (724) 586-6111, fax (724) 586-5151

emergency (724) 898-2481,  <mailto:[email protected]> 
[email protected],  <http://www.jandjfire.com> www.jandjfire.com 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120622/28498e45/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 862 bytes
Desc: not available
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120622/28498e45/attachment.gif>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to