Sprigs can stay but the pipe (which I assume are branchlines), must go. 

----- Original Message -----
From: Jarron Gass [mailto:[email protected]]
Sent: Monday, June 25, 2012 03:40 PM
To: [email protected] <[email protected]>; [email protected] 
<[email protected]>
Subject: RE: 3/4" Pipe and Sprigs

This originated with a building my company was looking at for a new owner.
The existing building was from the 1930's and has the existence of 3/4" pipe
on the end of the pipe scheduled lines as well as some 3/4" sprigs.  I was
looking for insight on whether the pipe could remain or needed to be changed
as well as whether the sprigs could remain.  Duane pointed out some sections
in NFPA which don't allow pipe smaller than 1" on revamped pipe schedule
systems.  The info I have received so far tends to lead me to change out all
3/4" pipe, since the system is going to be revamped.

Thanks,

Jarron

Jarron J. Gass - J. & J. Fire Protection Co., Inc.
101 Powell Rd., Butler, PA 16002, (724) 586-6111, fax (724) 586-5151
emergency (724) 898-2481, [email protected], www.jandjfire.com 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mike Hill
Sent: Monday, June 25, 2012 3:29 PM
To: [email protected]
Subject: RE: 3/4" Pipe and Sprigs

I missed the beginning of this conversation. Didn't NFPA-13 add CPVC and
copper pipe in the seismic load tables and aren't you allowed to use 3/4"
CPVC and copper in some situations?

Mike Hill

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson,
Duane (NIH/OD/ORS) [C]
Sent: Monday, June 25, 2012 2:50 PM
To: [email protected]
Subject: RE: 3/4" Pipe and Sprigs

What I am getting at is if you can't have that to begin with, why make a
special paragraph for seismic.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research
Services National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Brad Casterline [mailto:[email protected]]
Sent: Monday, June 25, 2012 2:18 PM
To: [email protected]
Subject: RE: 3/4" Pipe and Sprigs

It means the .5 or .75 x 0-4 nips are not allowed on re-vamp of existing
systems under seismic rules.
****************************************************************************
What confuses me is why does the following paragraph exist if 1" pipe is the
minimum size for hydraulic systems: 8.15.19.4.5  The use of pipe nipples
less than 1 in. (25 mm) in diameter shall not be permitted where seismic
design is required on the system.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to