What I am getting at is if you can't have that to begin with, why make a 
special paragraph for seismic.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Brad Casterline [mailto:[email protected]] 
Sent: Monday, June 25, 2012 2:18 PM
To: [email protected]
Subject: RE: 3/4" Pipe and Sprigs

It means the .5 or .75 x 0-4 nips are not allowed on re-vamp of existing
systems under seismic rules.
****************************************************************************
What confuses me is why does the following paragraph exist if 1" pipe is the
minimum size for hydraulic systems: 8.15.19.4.5  The use of pipe nipples
less than 1 in. (25 mm) in diameter
shall not be permitted where seismic design is required on the system.