You are correct.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: ParsleyConsulting [mailto:[email protected]] 
Sent: Monday, June 25, 2012 2:50 PM
To: [email protected]
Subject: Re: 3/4" Pipe and Sprigs

And that suggests to me that if the building Jarron is working on is not 
in an area where seismic protection is required that the use of the 3/4" 
pipe nipples is allowed.  Have I got that wrong?

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[email protected] <mailto:[email protected]>e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website



On 6/25/2012 11:18 AM, Brad Casterline wrote:
> It means the .5 or .75 x 0-4 nips are not allowed on re-vamp of existing
> systems under seismic rules.
> ****************************************************************************
> What confuses me is why does the following paragraph exist if 1" pipe is the
> minimum size for hydraulic systems: 8.15.19.4.5  The use of pipe nipples
> less than 1 in. (25 mm) in diameter
> shall not be permitted where seismic design is required on the system.
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to