I missed the beginning of this conversation. Didn't NFPA-13 add CPVC and
copper pipe in the seismic load tables and aren't you allowed to use 3/4"
CPVC and copper in some situations?

Mike Hill

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson,
Duane (NIH/OD/ORS) [C]
Sent: Monday, June 25, 2012 2:50 PM
To: [email protected]
Subject: RE: 3/4" Pipe and Sprigs

What I am getting at is if you can't have that to begin with, why make a
special paragraph for seismic.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research
Services National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Brad Casterline [mailto:[email protected]]
Sent: Monday, June 25, 2012 2:18 PM
To: [email protected]
Subject: RE: 3/4" Pipe and Sprigs

It means the .5 or .75 x 0-4 nips are not allowed on re-vamp of existing
systems under seismic rules.
****************************************************************************
What confuses me is why does the following paragraph exist if 1" pipe is the
minimum size for hydraulic systems: 8.15.19.4.5  The use of pipe nipples
less than 1 in. (25 mm) in diameter shall not be permitted where seismic
design is required on the system.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to