This has been a good discussion. Determining the required protection of
storages is not an easy task.  When you throw in the various hazards of an
auto parts store, it raises the ante even higher. 
However, the approach to solving the "problem" is no different than any
other. 
The starting point is good collection of information- identifying the
planned storage configurations and commodities. Too often (IMHO) we tend to
jump right into NFPA13. We need to spend the necessary time in the referring
documents (IBC, IFC, IMC, etc.) We only get to apply the referenced
codes/standards "to the prescribed extent of each such reference" (IFC
102.8).
Is it high piled storage? Look at Chpt 23 for definitions and then proceed
narrow it to rack or shelf.  Identify the commodities- Figure 2303.7.4 will
help define the commodity if it is limited quantities of Group A.  
As a FPE and having been the AHJ, I'm less concerned with whether the final
answer "seemed" correct, and more interested in how you arrived at the
answer- following the bouncing ball, as it were.
The EOR has a responsibility to provide the details and supporting analysis
arriving to their conclusion. The AHJ has the responsibility to review it
for compliance to the applicable code.  If they find holes, they need to
clearly identify what was missing, or what sections were improperly used.
Policing the storage configuration (height, aisles, commodities, etc.) is a
real world issue. The 2009 edition helped with storage height by allowing
the AHJ to require a visual indicator (IFC 2305.6). The design is based on
the "planned" storage arrangement.  The permit is issued based on that
planned storage arrangement.  The Certificate of Occupancy is based on the
actual conditions being within the limits of the approved plans. If the
conditions change, then a correction notice is issued, just like any other
occupancy.  Good documentation in the plan review files, and the
occupancy/storage permit will go a long ways.

Travis


------------------------------------------------
Travis E. Allen, P.E.
AEGIS Engineering, PLLC
(425) 745-4700 office