OK, well in his defense. He doesn't have anything other than a sprinkler drawing showing a max 12' storage height. The EOR has not provided the basis of his design criteria, ie , the OIC. In addition, he can drive 4 miles and walk in another identical store - same chain and see how they are storing.
To make things worse, the Sprinkler guy sent the AHJ 3 documents to prove the OH2 - 1) A Coffee Break Training sheet - one page only that discuss flue spaces, of which there are one in this facility 2) A page from NFPA #13 Chapter 16 - Rack Storage - and has two passages marked - one is about column protection not being needed if in racks are provided ( there are no in rack sprinklers, and the column protection is not the issue and the other is about foam protection - again not provided) 3) the table from chapter 13 with OH2 circled for 10-12' storage in palletized, bin box and shelf configuration - again, by definition this is not shelf storage. Therefore, the AHJ feels like somebody is blowing smoke and that pretty much ticks him off. Greg On Fri, Aug 17, 2012 at 8:19 AM, Cahill, Christopher <[email protected]>wrote: > AHJ meaning some gov't official. > > 'It falls to the AHJ to enforce the 12' storage height.' True > > 'Can an AHJ reject a plan that meets stated maximum storage height > criteria because he thinks someone might exceed that?' Absolutely not, just > as the police can't give you a ticket because you drive a Mustang that is > capable of (far) exceeding the speed limit. > > 'he can ask that they remove the top shelf', absolutely not, the shelf is > not an apparent violation. > > 'Many large box stores have lines painted on the walls to indicate maximum > storage height.' True, but that's a communication tool between owner and > employees, an AHJ cannot require or enforce the presence of the line. > > Chris Cahill, PE* > Senior Fire Protection Engineer, Aviation & Facilities Group > Burns & McDonnell > 8201 Norman Center Drive > Bloomington, MN 55437 > Phone: 952.656.3652 > Fax: 952.229.2923 > [email protected] > www.burnsmcd.com > > Proud to be one of FORTUNE's 100 Best Companies to Work For > *Registered in: MN > > > > > -----Original Message----- > From: [email protected] [mailto: > [email protected]] On Behalf Of Mike Hill > Sent: Friday, August 17, 2012 8:02 AM > To: [email protected] > Subject: RE: solid shelves in auto parts stores > > My first thought on seeing this was mercantile space (OH2) with > miscellaneous storage of higher commodities. Depending on height and > storage method this could also be OH2. Of course a lot more research needs > to be done on materials and method of storage to determine if the > miscellaneous storage section could be applied. > > IMO if it is designed for 12' storage and 12' maximum storage height is > clearly called for on the drawings it is the owner/tenant responsibility to > maintain 12' storage height. It falls to the AHJ to enforce the 12' storage > height. Many large box stores have lines painted on the walls to indicate > maximum storage height. Can an AHJ reject a plan that meets stated maximum > storage height criteria because he thinks someone might exceed that? He can > make it clear that 12' is the maximum storage height, he can ask that they > remove the top shelf and he can let the owner/tenant know the penalty for > exceeding the maximum height. The penalty, I guess, could include the > closing of the store until the violation is corrected. > > Mike Hill > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Greg > McGahan > Sent: Thursday, August 16, 2012 3:14 PM > To: [email protected] > Subject: solid shelves in auto parts stores > > Hello, > > 1) There is a PE involved > 2) This is not my job, but I am trying to be a friend to the AHJ' > 3) I can't readily put my hands on this due to other issues > > > A local AHJ has called me to inquire about the requirement for protecting > a major chain Auto Parts Store. The PE has stated OH2 throughout the store. > AHJ is asking questions because there are 12' tall racks with a solid top > making him think they will store over 12'. > > Questions, > > Are solid shelves allowed in racks aver 30" deep in this scenario without > protection in the racks? > > Is OH@ appropriate for these "typical" Auto Parts Stores with the storage > as it is? > > Thanks for your help if you have time, if not please ignore and have a > great day! > > > > > -- > Greg McGahan > Living Water Fire Protection, LLC <http://www.livingwaterfp.com> > 1160 McKenzie Road > Cantonment, FL 32533 > 850-937-1850 > fax 850-937-1852 > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: > < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment > s/20120816/ec9499ea/attachment.html> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -- Greg McGahan Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120817/e906c221/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum