My comments were not necessarily directed at your situation.  My comment were 
strictly meant in response to Mike's, which, with all due respect, I didn't 
agree with. 

Your AHJ is probably correct.  What he CAN do is tell them he disagrees with 
this being shelf storage and cite the reason in code why (too wide I think you 
said).  Cite he disagrees with Class IV.  Cite the other store and typical 
commodities and the definition of Class IV vs. Group A plastics.  That he can 
reject on.  Then he can go on to raise IFC possible HPS issue if over 6' of 
group A plastics. 

I think you are in FL?  Is the EOR required to submit the BOD?  Are the plans 
required to be PE stamped?  If so can't he just never open the plan and reject 
on the basis of no BOD?  Where's the owners certificate, assuming you have that 
edition adopted.  

I never meant to say the AHJ didn't have options.  Just certain tools are legal 
and certain tools are not.  I never once lost a case with the above process. 

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Friday, August 17, 2012 8:31 AM
To: [email protected]
Subject: Re: solid shelves in auto parts stores

OK, well  in his defense. He doesn't have anything other than a sprinkler 
drawing showing a max 12' storage height. The EOR has not provided the basis of 
his design criteria, ie , the OIC. In addition, he can drive 4 miles and walk 
in another identical store - same chain and see how they are storing.

To make things worse, the Sprinkler guy sent the AHJ 3 documents to prove the 
OH2 -

1)  A Coffee Break Training sheet - one page only that discuss flue spaces, of 
which there are one in this facility
2) A page from NFPA #13 Chapter 16 - Rack Storage - and has two passages marked 
- one is about column protection not being needed if in racks are provided ( 
there are no in rack sprinklers, and the column protection is not the issue and 
the other is about foam protection - again not provided)
3) the table from chapter 13 with OH2 circled for 10-12' storage in palletized, 
bin box and shelf configuration - again, by definition this is not shelf 
storage.

Therefore, the AHJ feels like somebody is blowing smoke and that pretty much 
ticks him off.

Greg

On Fri, Aug 17, 2012 at 8:19 AM, Cahill, Christopher
<[email protected]>wrote:

> AHJ meaning some gov't official.
>
> 'It falls to the AHJ to enforce the 12' storage height.'  True
>
> 'Can an AHJ reject a plan that meets stated maximum storage height 
> criteria because he thinks someone might exceed that?' Absolutely not, 
> just as the police can't give you a ticket because you drive a Mustang 
> that is capable of (far) exceeding the speed limit.
>
> 'he can ask that they remove the top shelf', absolutely not, the shelf 
> is not an apparent violation.
>
> 'Many large box stores have lines painted on the walls to indicate 
> maximum storage height.' True, but that's a communication tool between 
> owner and employees, an AHJ cannot require or enforce the presence of the 
> line.
>
> Chris Cahill, PE*
> Senior Fire Protection Engineer, Aviation & Facilities Group Burns & 
> McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
>
> Proud to be one of FORTUNE's 100 Best Companies to Work For 
> *Registered in: MN
>
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Mike Hill
> Sent: Friday, August 17, 2012 8:02 AM
> To: [email protected]
> Subject: RE: solid shelves in auto parts stores
>
> My first thought on seeing this was mercantile space (OH2) with 
> miscellaneous storage of higher commodities. Depending on height and 
> storage method this could also be OH2. Of course a lot more research 
> needs to be done on materials and method of storage to determine if 
> the miscellaneous storage section could be applied.
>
> IMO if it is designed for 12' storage and 12' maximum storage height 
> is clearly called for on the drawings it is the owner/tenant 
> responsibility to maintain 12' storage height. It falls to the AHJ to 
> enforce the 12' storage height. Many large box stores have lines 
> painted on the walls to indicate maximum storage height. Can an AHJ 
> reject a plan that meets stated maximum storage height criteria 
> because he thinks someone might exceed that? He can make it clear that 
> 12' is the maximum storage height, he can ask that they remove the top 
> shelf and he can let the owner/tenant know the penalty for exceeding 
> the maximum height. The penalty, I guess, could include the closing of the 
> store until the violation is corrected.
>
> Mike Hill
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Greg 
> McGahan
> Sent: Thursday, August 16, 2012 3:14 PM
> To: [email protected]
> Subject: solid shelves in auto parts stores
>
> Hello,
>
> 1) There is a PE involved
> 2) This is not my job, but I am trying to be a friend to the AHJ'
> 3) I can't readily put my hands on this due to other issues
>
>
> A local AHJ has called me to inquire about the requirement for 
> protecting a major chain Auto Parts Store. The PE has stated OH2 throughout 
> the store.
> AHJ is asking questions because there are 12' tall racks with a solid 
> top making him think they will store over 12'.
>
> Questions,
>
> Are solid shelves allowed in racks aver 30" deep in this scenario 
> without protection in the racks?
>
> Is OH@ appropriate for these "typical" Auto Parts Stores with the 
> storage as it is?
>
> Thanks for your help if you have time, if not please ignore and have a 
> great day!
>
>
>
>
> --
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL:
> <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
> hment
> s/20120816/ec9499ea/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120817/e906c221/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to