AHJ meaning some gov't official. 

'It falls to the AHJ to enforce the 12' storage height.'  True

'Can an AHJ reject a plan that meets stated maximum storage height criteria 
because he thinks someone might exceed that?' Absolutely not, just as the 
police can't give you a ticket because you drive a Mustang that is capable of 
(far) exceeding the speed limit.

'he can ask that they remove the top shelf', absolutely not, the shelf is not 
an apparent violation. 

'Many large box stores have lines painted on the walls to indicate maximum 
storage height.' True, but that's a communication tool between owner and 
employees, an AHJ cannot require or enforce the presence of the line. 

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mike Hill
Sent: Friday, August 17, 2012 8:02 AM
To: [email protected]
Subject: RE: solid shelves in auto parts stores

My first thought on seeing this was mercantile space (OH2) with miscellaneous 
storage of higher commodities. Depending on height and storage method this 
could also be OH2. Of course a lot more research needs to be done on materials 
and method of storage to determine if the miscellaneous storage section could 
be applied.

IMO if it is designed for 12' storage and 12' maximum storage height is clearly 
called for on the drawings it is the owner/tenant responsibility to maintain 
12' storage height. It falls to the AHJ to enforce the 12' storage height. Many 
large box stores have lines painted on the walls to indicate maximum storage 
height. Can an AHJ reject a plan that meets stated maximum storage height 
criteria because he thinks someone might exceed that? He can make it clear that 
12' is the maximum storage height, he can ask that they remove the top shelf 
and he can let the owner/tenant know the penalty for exceeding the maximum 
height. The penalty, I guess, could include the closing of the store until the 
violation is corrected.

Mike Hill

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, August 16, 2012 3:14 PM
To: [email protected]
Subject: solid shelves in auto parts stores

Hello,

1) There is a PE involved
2) This is not my job, but I am trying to be a friend to the AHJ'
3) I can't readily put my hands on this due to other issues


A local AHJ has called me to inquire about the requirement for protecting a 
major chain Auto Parts Store. The PE has stated OH2 throughout the store.
AHJ is asking questions because there are 12' tall racks with a solid top 
making him think they will store over 12'.

Questions,

Are solid shelves allowed in racks aver 30" deep in this scenario without 
protection in the racks?

Is OH@ appropriate for these "typical" Auto Parts Stores with the storage as it 
is?

Thanks for your help if you have time, if not please ignore and have a great 
day!




--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120816/ec9499ea/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________