My first thought on seeing this was mercantile space (OH2) with
miscellaneous storage of higher commodities. Depending on height and storage
method this could also be OH2. Of course a lot more research needs to be
done on materials and method of storage to determine if the miscellaneous
storage section could be applied.

IMO if it is designed for 12' storage and 12' maximum storage height is
clearly called for on the drawings it is the owner/tenant responsibility to
maintain 12' storage height. It falls to the AHJ to enforce the 12' storage
height. Many large box stores have lines painted on the walls to indicate
maximum storage height. Can an AHJ reject a plan that meets stated maximum
storage height criteria because he thinks someone might exceed that? He can
make it clear that 12' is the maximum storage height, he can ask that they
remove the top shelf and he can let the owner/tenant know the penalty for
exceeding the maximum height. The penalty, I guess, could include the
closing of the store until the violation is corrected.

Mike Hill

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, August 16, 2012 3:14 PM
To: [email protected]
Subject: solid shelves in auto parts stores

Hello,

1) There is a PE involved
2) This is not my job, but I am trying to be a friend to the AHJ'
3) I can't readily put my hands on this due to other issues


A local AHJ has called me to inquire about the requirement for protecting a
major chain Auto Parts Store. The PE has stated OH2 throughout the store.
AHJ is asking questions because there are 12' tall racks with a solid top
making him think they will store over 12'.

Questions,

Are solid shelves allowed in racks aver 30" deep in this scenario without
protection in the racks?

Is OH@ appropriate for these "typical" Auto Parts Stores with the storage as
it is?

Thanks for your help if you have time, if not please ignore and have a great
day!




--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120816/ec9499ea/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to