What's the purpose of these "local alarms" ?, to alert the dwelling unit
occupants ?  First and foremost is a fire alarm system required in this
building in accordance with IBC 907 ? If so then a fire alarm system is
required pursuant to IBC 907 and accordingly notification appliances in
accordance with IBC 907.5.  If this is a jurisdictional dwelling unit
occupant notification requirement outside the model code consider my
previous comment to interconnect the waterflow switch with the dwelling
unit smoke alarms which already meet the prescribed notification
requirements of the IBC and or IRC. 

Hope this helps,

John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Borough of Red Bank, New Jersey
Office: 732-530-2760 X 331
Cell/Text: 732-904-6823
Email: [email protected]
http://www.redbanknj.org





CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to