My contract does not include alarms, only the sprinklers. It will be up to the 
owner and the FM to work that detail out. I have been asked to show a strobe 
outside and a local interior alarm on the drawing. My original post was asking 
for a specific product in a small, reasonably unobtrusive alarm to install in a 
hallway. 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com

On May 29, 2013, at 5:08 PM, "John Drucker - Home" <[email protected]> 
wrote:

> Todd,  How old are the smoke alarms ?, at 10 yrs. their due for replacement
> anyway.
> 
> As I commented earlier, a prescriptive way to solve the issue.
> 
> John Drucker, CET
> Fire Protection Subcode Official
> Fire / Building / Electrical Inspector
> New Jersey
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Todd -
> Work
> Sent: Wednesday, May 29, 2013 4:25 PM
> To: [email protected]
> Subject: Re: 13R local alarm
> 
> The FM asked for the sprinkler alarms to be connected to ring the smoke
> detectors. I asked if a separate bell would be acceptable. The present
> system is essentially residential hard wired smokes. I'm not sure if all of
> the devices in each unit go off when one activates. There is no
> annunciation. I don't think the detectors are wired to accept additional
> input, so the entire system would have to be replaced if we have to
> interconnect. Right now they are not being asked to upgrade the alarms and
> this is not a town with a wimpy fire marshal.
> 
> The alarm system is beyond my contract and the drawing notes state so. That
> is a can of worms I will let someone else open.
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 
> On May 29, 2013, at 3:07 PM, "Tom Duross" <[email protected]> wrote:
> 
>> We had a local town home rule go into effect 15+ years ago requiring 
>> sprinklers in anything 3+ units "substantially" renovated but it 
>> forgot to mention annunciation (also forgot water supply).  Many slick 
>> property owners got together and sued and after the dust settled, it 
>> was decided to put an electric bell in the stair lobby or main lobby 
>> of each unit plus the outside.  No formal fire alarm was required.
>> I've done the accessory relay to wire a dry contact to a 3 wire 120 
>> vac smoke circuit but it voids the listing of the smokes, or did (been 
>> many years).
>> These days Todd, I don't know how you could install a sprinkler system 
>> under current MA code and not have to install a formal 72 FA.  3 units 
>> or more requires supervision and central station in MA.
>> TD
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of 
>> Mike Henke
>> Sent: Wednesday, May 29, 2013 11:43 AM
>> To: [email protected]; 
>> [email protected]
>> Subject: RE: 13R local alarm
>> 
>> It may be possible to activate both the smoke alarms and a separate 
>> waterflow alarm.
>> The flowswitch should have 2 sets of contacts.
>> One switch can activate a local alarm such as the 120 vac mini horn 
>> The other switch may be able to activate the smoke alarms.
>> 
>> This would provide the additional signal for waterflow so it wouldn't 
>> be confused with burnt toast.
>> 
>> You probably have to contact the detector manufacturer to see how and 
>> if the detectors can be activated from a separate switch. They may 
>> have a separate module for this.
>> There are some products on the market for this such as Firex but I 
>> don't know if they universally work with all makes and models of smoke
> alarms.
>> There was also a carrier frequency device made by Cepco products for this.
>> 
>> Regards,
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to