The FM asked for the sprinkler alarms to be connected to ring the smoke detectors. I asked if a separate bell would be acceptable. The present system is essentially residential hard wired smokes. I'm not sure if all of the devices in each unit go off when one activates. There is no annunciation. I don't think the detectors are wired to accept additional input, so the entire system would have to be replaced if we have to interconnect. Right now they are not being asked to upgrade the alarms and this is not a town with a wimpy fire marshal.
The alarm system is beyond my contract and the drawing notes state so. That is a can of worms I will let someone else open. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com On May 29, 2013, at 3:07 PM, "Tom Duross" <[email protected]> wrote: > We had a local town home rule go into effect 15+ years ago requiring > sprinklers in anything 3+ units "substantially" renovated but it forgot to > mention annunciation (also forgot water supply). Many slick property owners > got together and sued and after the dust settled, it was decided to put an > electric bell in the stair lobby or main lobby of each unit plus the > outside. No formal fire alarm was required. > I've done the accessory relay to wire a dry contact to a 3 wire 120 vac > smoke circuit but it voids the listing of the smokes, or did (been many > years). > These days Todd, I don't know how you could install a sprinkler system under > current MA code and not have to install a formal 72 FA. 3 units or more > requires supervision and central station in MA. > TD > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Mike > Henke > Sent: Wednesday, May 29, 2013 11:43 AM > To: [email protected]; [email protected] > Subject: RE: 13R local alarm > > It may be possible to activate both the smoke alarms and a separate > waterflow alarm. > The flowswitch should have 2 sets of contacts. > One switch can activate a local alarm such as the 120 vac mini horn The > other switch may be able to activate the smoke alarms. > > This would provide the additional signal for waterflow so it wouldn't be > confused with burnt toast. > > You probably have to contact the detector manufacturer to see how and if the > detectors can be activated from a separate switch. They may have a separate > module for this. > There are some products on the market for this such as Firex but I don't > know if they universally work with all makes and models of smoke alarms. > There was also a carrier frequency device made by Cepco products for this. > > Regards, > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org