Todd,  How old are the smoke alarms ?, at 10 yrs. their due for replacement
anyway.

As I commented earlier, a prescriptive way to solve the issue.

John Drucker, CET
Fire Protection Subcode Official
Fire / Building / Electrical Inspector
New Jersey



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd -
Work
Sent: Wednesday, May 29, 2013 4:25 PM
To: [email protected]
Subject: Re: 13R local alarm

The FM asked for the sprinkler alarms to be connected to ring the smoke
detectors. I asked if a separate bell would be acceptable. The present
system is essentially residential hard wired smokes. I'm not sure if all of
the devices in each unit go off when one activates. There is no
annunciation. I don't think the detectors are wired to accept additional
input, so the entire system would have to be replaced if we have to
interconnect. Right now they are not being asked to upgrade the alarms and
this is not a town with a wimpy fire marshal.

The alarm system is beyond my contract and the drawing notes state so. That
is a can of worms I will let someone else open.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com

On May 29, 2013, at 3:07 PM, "Tom Duross" <[email protected]> wrote:

> We had a local town home rule go into effect 15+ years ago requiring 
> sprinklers in anything 3+ units "substantially" renovated but it 
> forgot to mention annunciation (also forgot water supply).  Many slick 
> property owners got together and sued and after the dust settled, it 
> was decided to put an electric bell in the stair lobby or main lobby 
> of each unit plus the outside.  No formal fire alarm was required.
> I've done the accessory relay to wire a dry contact to a 3 wire 120 
> vac smoke circuit but it voids the listing of the smokes, or did (been 
> many years).
> These days Todd, I don't know how you could install a sprinkler system 
> under current MA code and not have to install a formal 72 FA.  3 units 
> or more requires supervision and central station in MA.
> TD
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> Mike Henke
> Sent: Wednesday, May 29, 2013 11:43 AM
> To: [email protected]; 
> [email protected]
> Subject: RE: 13R local alarm
> 
> It may be possible to activate both the smoke alarms and a separate 
> waterflow alarm.
> The flowswitch should have 2 sets of contacts.
> One switch can activate a local alarm such as the 120 vac mini horn 
> The other switch may be able to activate the smoke alarms.
> 
> This would provide the additional signal for waterflow so it wouldn't 
> be confused with burnt toast.
> 
> You probably have to contact the detector manufacturer to see how and 
> if the detectors can be activated from a separate switch. They may 
> have a separate module for this.
> There are some products on the market for this such as Firex but I 
> don't know if they universally work with all makes and models of smoke
alarms.
> There was also a carrier frequency device made by Cepco products for this.
> 
> Regards,
> 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to