But what if the underground is a loop and has section valves plus the riser 
valves? The Phoenix Fire Dept. makes us put a FDC on each manifold instead of 
at the fire pump. The pump supplies the underground loop for the entire 
building with multiple lead ins. There are sectional gate valves in the loop, 
there is a gate valve in each underground leadin, and there are gate valves in 
each riser on a manifold. Phoenix says we can't have any gate valves between 
the FDC and the "system" gate valves. They read 8.17.2.4.3 and stop there. As 
far as the PFD is concerned 8.17.2.4.4 doesn't apply.

What do you guys think? Can there be multiple gate valves between the FDC and 
sprinkler systems?

Ron F   

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Charles 
Thurston
Sent: Thursday, July 11, 2013 3:27 PM
To: [email protected]
Subject: Re: FDC Arrangement

Hello All,

I tend to use these for these situations  8.17.2.4.4 is the key to them.

8.17.2.4.2   For single systems, the fire department connection shall be 
installed  as follows:

(1)  Wet system - on the system side of system control, check, and alarm valves 
(see Figure A.8.16.1.1)
(2)  Dry system - between  the  system control valve and  the dry pipe valve
(3)  Preaction system - between  the preaction valve and the check valve on the 
system side of the preaction valve
(4)  Deluge system - on the system side of the deluge  valve

8.17.2.4.3   For multiple systems, the fire department connection shall be 
connected between 
the supply control valves and the system control valves.

8.17.2.4.4* The requirements of 8.17.2.4.2 and 8.17.2.4.3 shall not apply where 
the fire department connection is connected to the underground piping.






-- 
Best regards,
 Charles                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to