Charles, I would be careful. You can't use 1/2" nipples in an earthquake zone 
(8.15.19.4.4). Given your proximity to Charleston, this may be a concern. I 
would assume street elbows (if permitted) would fall under the same category. 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On Jan 17, 2014, at 5:05 PM, Kenneth Berman <[email protected]> wrote:
> 
> close nipples are as close as street ells. 1/2 x 1/2 x 1 tees and you can
> leave the uprights, or for tight spaces where you can eliminate the
> upright, use 1 x 1 x 1/2 with a 1" plug.
> 
> 
> On Fri, Jan 17, 2014 at 3:54 PM, Charles Thurston <[email protected]>wrote:
> 
>> Hello All,
>> 
>> I do wish I could find some 1/2" Male x 1" Female Street ells for a
>> upright to pendant conversion project.
>> 
>> Friday, January 17, 2014, 4:25:23 PM, you wrote:
>> 
>>> I think it comes down to if the street elbows are made according to
>>> the appropriate ASTM standard from Table 6.4.1. In your defense,
>>> 6.4.6.1 states that unless circumstances exist where hex bushings
>>> are allowed, one piece reducer fittings shall be used for a change in
>> pipe size.
>> 
>>> Todd G Williams, PE
>>> Fire Protection Design/Consulting
>>> Stonington, CT
>>> www.fpdc.com
>>> 860-535-2080 (ofc)
>> 
>>>> On Jan 17, 2014, at 3:43 PM, "Morey, Mike" <[email protected]> wrote:
>> 
>>>> So I seem to remember this being a "no-no" but the code doesn't seem to
>> explicitly prohibit us from using them.  I have a tight squeeze where a 1"
>> male x female "street" elbow would be helpful, but I want to make sure I'm
>> not missing something in 13 that prohibits it, we use the 2010 edition.
>> 
>> 
>>>> Mike Morey, CFPS, SET
>>>> Planner Scheduler/Designer
>>>> BMWC Constructors, Inc.
>>>> 1740 W. Michigan St, Indianapolis, IN 46222
>>>> O: 317.651.0596 | C: 317.586.8111
>>>> [email protected]<mailto:[email protected]> | www.bmwc.com<
>> http://www.bmwc.com/>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> 
>> 
>> --
>> Best regards,
>> Charles Thurston                          mailto:[email protected]
>> Systems Design Manager
>> NICET Certified
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to