I thought this was about using 1" st ells in a tight spot, not changing uprights to pendants. And of course you can use them and they're readily available through plumbing suppliers if your sprinkler supplier doesn't have them. They come in reducing types, in black steel, galvy, stainless, bronze, and in weights (strength) equivalent to schedule 40, 80, 120 & 160. Very common for industrial boiler application.
Sent from my iPhone > On Jan 17, 2014, at 2:23 PM, Todd - Work <[email protected]> wrote: > > Charles, I would be careful. You can't use 1/2" nipples in an earthquake zone > (8.15.19.4.4). Given your proximity to Charleston, this may be a concern. I > would assume street elbows (if permitted) would fall under the same category. > > Todd G Williams, PE > Fire Protection Design/Consulting > Stonington, CT > www.fpdc.com > 860-535-2080 (ofc) > >> On Jan 17, 2014, at 5:05 PM, Kenneth Berman <[email protected]> wrote: >> >> close nipples are as close as street ells. 1/2 x 1/2 x 1 tees and you can >> leave the uprights, or for tight spaces where you can eliminate the >> upright, use 1 x 1 x 1/2 with a 1" plug. >> >> >> On Fri, Jan 17, 2014 at 3:54 PM, Charles Thurston <[email protected]>wrote: >> >>> Hello All, >>> >>> I do wish I could find some 1/2" Male x 1" Female Street ells for a >>> upright to pendant conversion project. >>> >>> Friday, January 17, 2014, 4:25:23 PM, you wrote: >>> >>>> I think it comes down to if the street elbows are made according to >>>> the appropriate ASTM standard from Table 6.4.1. In your defense, >>>> 6.4.6.1 states that unless circumstances exist where hex bushings >>>> are allowed, one piece reducer fittings shall be used for a change in >>> pipe size. >>> >>>> Todd G Williams, PE >>>> Fire Protection Design/Consulting >>>> Stonington, CT >>>> www.fpdc.com >>>> 860-535-2080 (ofc) >>> >>>>> On Jan 17, 2014, at 3:43 PM, "Morey, Mike" <[email protected]> wrote: >>> >>>>> So I seem to remember this being a "no-no" but the code doesn't seem to >>> explicitly prohibit us from using them. I have a tight squeeze where a 1" >>> male x female "street" elbow would be helpful, but I want to make sure I'm >>> not missing something in 13 that prohibits it, we use the 2010 edition. >>> >>> >>>>> Mike Morey, CFPS, SET >>>>> Planner Scheduler/Designer >>>>> BMWC Constructors, Inc. >>>>> 1740 W. Michigan St, Indianapolis, IN 46222 >>>>> O: 317.651.0596 | C: 317.586.8111 >>>>> [email protected]<mailto:[email protected]> | www.bmwc.com< >>> http://www.bmwc.com/> >>>>> _______________________________________________ >>>>> Sprinklerforum mailing list >>>>> [email protected] >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >>>> _______________________________________________ >>>> Sprinklerforum mailing list >>>> [email protected] >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >>> >>> >>> >>> -- >>> Best regards, >>> Charles Thurston mailto:[email protected] >>> Systems Design Manager >>> NICET Certified >>> >>> _______________________________________________ >>> Sprinklerforum mailing list >>> [email protected] >>> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org