I was not surprised at the first e-mail, that's what I hear all the time...  
"the plan reviewer approved the plans", (even though they had significant 
technical errors).


Had me goin' for a minute.  

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland 
Huggins
Sent: Monday, January 20, 2014 2:39 PM
To: [email protected]
Subject: Re: 1/2" and Seismic

CORRECTION

that should read - an approved set of plans does NOT mean it's ok to violate 
NFPA 13.   I've gotta lay off the coffee.

Thanks John for the rapid catch and polite direct contact.

Roland
  
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Jan 20, 2014, at 11:33 AM, Roland Huggins <[email protected]> wrote:

> DOn't forget that an approved set of plans means it is ok to violate NFPA 13. 
>  All an approved set of plans means is that you have permission to proceed. 
> So, even when approved, if you install it, you are responsible for it being 
> right.    Now if there is an existing approved variance, all is golden.
> 
> Roland
> 
> 
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
> 
> 
> 
> 
> 
> On Jan 17, 2014, at 3:52 PM, Charles Thurston <[email protected]> wrote:
> 
>> This is an existing system. 1 1/2" branch with 1/2" outlet "T"s for heads, 
>> They added a L/O ceiling 6" below the top of the pipe in the parking deck. 
>> Now need to nipple over to a Dry Wax Over Lead (Local Ordnance) Dry Head. 
>> Another contractor submitted plans, calcs and got a permit for this a 1/2" 
>> Close, 1/2" x 1" 90, 1' Close nipple, 1" T with plug for the head. The other 
>> contractor's foreman smarted off to one of the owners and they got thrown 
>> off the site. Material is all there, Just need the labor to put it in.
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to