You hit it on the nose when indicating that the 1" restriction is on PIPE.  
Does this limit apply to fittings?  Well the real question since we know 1/2" 
outlets are ok is not the standard fitting but nipple extensions.  That's an 
issue that the standard has not yet addressed.  There have been cases where 2 
or 3 extensions have been combined (and probably not included in the 
calculations).  I believe something on it will be in the next addition.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org