You hit it on the nose when indicating that the 1" restriction is on PIPE. Does this limit apply to fittings? Well the real question since we know 1/2" outlets are ok is not the standard fitting but nipple extensions. That's an issue that the standard has not yet addressed. There have been cases where 2 or 3 extensions have been combined (and probably not included in the calculations). I believe something on it will be in the next addition.
Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Jan 17, 2014, at 3:19 PM, Forest Wilson Fire Sprinkler Contractor <[email protected]> wrote: > I dont underatand how a fitting would be considered a pipe nipple. > The prohibition against using 1/2" pipe in earthquake zones should not apply > to the use of street l fittings. > > If it did, then the same argument could could made against using any 1/2" > fitting. > > > Forest Wilson _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org