Jerry,
The only reference I could find in NFPA 13 is not a direct requirement, but rather is annex material to support 6.2.6.1on areas where corrosion resistant sprinklers are required. One of the examples is "areas over and around swimming pools", which sort of suggest those areas are to be sprinklered.
    I haven't looked at the Building or Fire Code.
*

PARSLEY CONSULTING

*

Ken Wagoner

760.745.6181 voice

760.745.0537 fax

website: www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>

On 1/22/2014 2:19 PM, [email protected] wrote:
Guyz/Gals:


I know that, at one time, there was a 'blurb' about sprinkler protection over swimming 
pool areas. We have just spent a fairly significant amount of time looking for the 
'requirement' in recent editions of 13 - and have been unable to find a specific 
citation. Aside from "all areas are required to be sprinklered..." can anyone 
assist us with a specific reference to swimming pool areas (hotel/motels, et al) - in any 
Code - needing to be sprinkler protected. I remember reading about the possibility of the 
pool being emptied and the pool itself and/or surrounding areas being used for 'storage' 
of combustible materials, but that was years ago...



Any assistance will be much appreciated - we are performing a third-party 
review and our PE/FPE is stuck.



Regards to All. Gracias!!




Jerry
[email protected]


Jerry D. Watts, SFPE
President & Co-Founder
ACCENT FIRE ENGINEERING INT'L. Ltd.
Santa Fe, New Mexico USA








-----Original Message-----
From: Brian Harris <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Wed, Jan 22, 2014 3:09 pm
Subject: RE: Reusing Heads


Thanks!

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Wednesday, January 22, 2014 12:34 PM
To: [email protected]
Subject: RE: Reusing Heads

It's also in NFPA 25 for good measure.


Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Morey, Mike
Sent: Wednesday, January 22, 2014 9:25 AM
To: [email protected]
Subject: RE: Reusing Heads

In 2013 6.2.1 (and added clarification in section 6.2.1.1)

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
[email protected] | www.bmwc.com

________________________________________
From: [email protected]
[[email protected]] on behalf of Brian Harris
[[email protected]]
Sent: Wednesday, January 22, 2014 12:17 PM
To: [email protected]
Subject: Reusing Heads

I know I've seen it somewhere but can someone point me to the section of
NFPA-13 that says once you remove a head you have to replace it with a new one?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________