Go to the Building Code:  (using 2009 for reference)

Swimming pool without spectator is an A-3 occupancy. [Section 303]

Table 503 sets limitations on areas for A-3 occupancies based on building 
construction types.

So sprinklers may or may not be required based on whether you are under or over 
the area limit.

So for example, for a Type IIA construction you can go  15,500 sq. ft, beyond 
that you have to provide sprinklers. See Section 507.6, 2. for additional data 
on building area requirements.

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, January 22, 2014 5:19 PM
To: [email protected]
Subject: Re: Swimming Pools RFI

Guyz/Gals:


I know that, at one time, there was a 'blurb' about sprinkler protection over 
swimming pool areas. We have just spent a fairly significant amount of time 
looking for the 'requirement' in recent editions of 13 - and have been unable 
to find a specific citation. Aside from "all areas are required to be 
sprinklered..." can anyone assist us with a specific reference to swimming pool 
areas (hotel/motels, et al) - in any Code - needing to be sprinkler protected. 
I remember reading about the possibility of the pool being emptied and the pool 
itself and/or surrounding areas being used for 'storage' of combustible 
materials, but that was years ago...



Any assistance will be much appreciated - we are performing a third-party 
review and our PE/FPE is stuck.



Regards to All. Gracias!!




Jerry
[email protected]


Jerry D. Watts, SFPE
President & Co-Founder
ACCENT FIRE ENGINEERING INT'L. Ltd.
Santa Fe, New Mexico USA








-----Original Message-----
From: Brian Harris <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Wed, Jan 22, 2014 3:09 pm
Subject: RE: Reusing Heads


Thanks!

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Wednesday, January 22, 2014 12:34 PM
To: [email protected]
Subject: RE: Reusing Heads

It's also in NFPA 25 for good measure.


Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Morey, Mike
Sent: Wednesday, January 22, 2014 9:25 AM
To: [email protected]
Subject: RE: Reusing Heads

In 2013 6.2.1 (and added clarification in section 6.2.1.1)

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
[email protected] | www.bmwc.com

________________________________________
From: [email protected]
[[email protected]] on behalf of Brian Harris 
[[email protected]]
Sent: Wednesday, January 22, 2014 12:17 PM
To: [email protected]
Subject: Reusing Heads

I know I've seen it somewhere but can someone point me to the section of
NFPA-13 that says once you remove a head you have to replace it with a new one?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to