The state of Minnesota Fire code amended the IFC to read "Sprinkler protection need not be provided on the ceiling of rooms containing swimming pools when the pool area is used exclusively for swimming purposes and when sprinklers are provided around the perimeter of the pool area." Possible your state/jurisdiction has done something similar.
Reed A. Roisum, C.E.T. | Karges-Faulconbridge, Inc. | Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http://www.kfiengineers.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of rongreenman . Sent: Wednesday, January 22, 2014 4:54 PM To: [email protected] Subject: Re: Swimming Pools RFI The specific citation is that all areas need to be sprinklered. Couple that to all the areas that are specifically exempted, pools not being one, and the only possible interpretation is that pool areas must be sprinklered. On Wed, Jan 22, 2014 at 2:28 PM, ParsleyConsulting <[email protected]>wrote: > Jerry, > The only reference I could find in NFPA 13 is not a direct > requirement, but rather is annex material to support 6.2.6.1on areas > where corrosion resistant sprinklers are required. One of the > examples is "areas over and around swimming pools", which sort of > suggest those areas are to be sprinklered. > I haven't looked at the Building or Fire Code. > * > > PARSLEY CONSULTING > > * > > Ken Wagoner > > 760.745.6181 voice > > 760.745.0537 fax > > website: www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> > > > On 1/22/2014 2:19 PM, [email protected] wrote: > >> Guyz/Gals: >> >> >> I know that, at one time, there was a 'blurb' about sprinkler >> protection over swimming pool areas. We have just spent a fairly >> significant amount of time looking for the 'requirement' in recent >> editions of 13 - and have been unable to find a specific citation. >> Aside from "all areas are required to be sprinklered..." can anyone >> assist us with a specific reference to swimming pool areas >> (hotel/motels, et al) - in any Code - needing to be sprinkler >> protected. I remember reading about the possibility of the pool being >> emptied and the pool itself and/or surrounding areas being used for >> 'storage' of combustible materials, but that was years ago... >> >> >> >> Any assistance will be much appreciated - we are performing a >> third-party review and our PE/FPE is stuck. >> >> >> >> Regards to All. Gracias!! >> >> >> >> >> Jerry >> [email protected] >> >> >> Jerry D. Watts, SFPE >> President & Co-Founder >> ACCENT FIRE ENGINEERING INT'L. Ltd. >> Santa Fe, New Mexico USA _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org